de-humidification with a DX coil
I have an application where the outside design condition is 35°C, 75 % RH.
The room design condition is 22°C, 50 %RH. A relative small amount of outside air is supplied to the room (infiltration)
How do you indicate on the psychrometric cart the de-humidification process? How do you calculate the expected %RH in the room?
thks
thks
RE: de-humidification with a DX coil
---KenRad
Air at 95*f and 75%RH = 189.3 gr moisture/lb
enthalpy = 52,64btu/lb
SpV = 14,59 cu ft/lb
Room air
Air at 72*F and 50% RH = 58.38 gr moisture/lb
enthalpy = 26.4btu/lb
SpV = 13.58 cu ft/lb
per lb means weight of air moved
so if you remove the difference of moisture and heat between the two you should get the results you are looking for. Of course this doesn't account for infiltration.
http://www.coolit.co.za/psychart/
Will the de-humidification be possible with a DX-coil?
What psychrometric software could you recommend?
The psych chart can give good beginning-to-end conditions. Don't rely on your ruler lines to tell you what really happens inbetween. Cool: go straight, horizontal left until you hit the dew point (100% RH) line. Then follow the dew point line down until you hit the right leaving dry bulb temperature (vertical).
A DX coil or chilled water coil can dehumidify, BUT the DX poses more risk in that it cycles off during part load conditions. During off cycles, warm and humid air is brought in until cool surfaces that the cooling air produces sweat and cause condensation.
If DX is needed, look for multiple stage DX and hot gas bypass. One phenomenon about the psych chart is that it doesn't account for cooling coil bypass. Your resulting point isn't actually saturated, but close. Cooling coil bypass allows more dehumidification via a phenomena too difficult to explain here. As a result, typical coils will discharge 55°F air at about 90% (versus 100%) RH.
-CB
the thing is your room condition/ R/A changes from actual outside conditions to the actual design room condition as your initial Room condition aproximate thoe outside condition.
In other words: how do you indicate on the chart your initial point of 80% RH that must be dehumified to 50%RH, how do you represent this process line?
Mark the outside air condition and the required room condition on the psychrometric chart. Now get the ratio of sensible heat to the total heat(sensible heat + latent heat). You can find a protractor with sensible heat ratio slopes marked on it. Replicate the same line on the chart originating from the room condition and towards the saturation line. Now connect the ambient condition and the point where SHR line meets the saturation line(Actually this is a short cut to the process of extending a horizontal line from outside condition to saturation and then dropping it down along the saturation line to the required point)
Your actual room entry point depends upon the coil bypass factor. I suggest you to either take membership of ASHRAE(you will get one handbook free per year + one monthly journal free) for USD 150 or purchase the Handbooks. Other good reference is Principles of Air Conditioning by Shan K Wang.
You can download a good psychrometric calculator from http://pmilligan.net/pmtherm.htm but this will not help you in load calculations.
Mechanicaldup, the beginning to end I was referring to really meant an outside air condition to a steady state indoor air condition. You have a complex question. Best engineering practices available to non-Ph.D. types deal with steady state conditions at point A and point B, i.e., outdoor and indoor or return air. The lines you draw on the psych chart are between location A and location B, but NOT location B to location B ten minutes later. This is more complex. However, you can represent the before and after conditions on the psych chart by two different points, e.g., a space that started at 77°F, 55% RH and ended at 74°F, 52% RH. You can look at the two points and figure out the difference in anything (enthalpy, dew point, wet bulb, etc.) but the line between doesn't mean much of anything as far as rate of change, etc...
Does this make sense regarding your question, or am I off track?
Then you have to calculate the air entering the cooling coil conditions. You have to do mixed air calculations of the outdoor air with return air. You have to know their CFM. Use the outdoor design condition for the OA. Use room design condition plus return duct heat gain plus return air fan heat gain for the return air conditions.
The cooling coil duty is the the sensible and latent heat difference between coil entering and leaving conditions.
If you can calculate the above, it is a cinch plotting the state points on the psycrometric chart. The tricky part is making sure the cooling coil leaving condition is just below the saturation line.
See Carrier Airconditioning Design Handbook for the pschrometric formulas involved.
like ChasBean1 have noted, I am concerned about the transient from the start condition at ambient conditions to the final room condition. how to determine if equipment x would be able to dehumidify the space and wheter a de-humidifier is required in serie. and to determine in what time the space would be dehumidified. how do I handle this?
I am trying to figure out how determine the de-humidification effect.
for example for Room A
start condition
t1=35
RH1= 80%
after a certain time period
t2= 22°C
RH2=?
what kind/make of air handler is this?, cfm? tonage?
Wo is large suppliers of de-humidification equipment?
Trane has two good papers on the subject.
Here are the links:
http://www
http://w
Give me your feed back
SLB
I will have look at the trane literature