Reducing the "minimum frost" depth
2

Reducing the "minimum frost" depth

Reducing the "minimum frost" depth

(OP)
Might anyone have suggestions or information regarding an acceptable method of reducing the "minimum frost depth" (in this case ~ 42") utilizing light weight concrete or foam insulation?
Can either of these materials be used in an acceptable manner to achieve this goal? Might there be other methods available that I'm not aware of?

Thank you!
Thomas

RE: Reducing the "minimum frost" depth

Yes, insulating foundations is a proven method of reducing frost effects on foundations, allowing a shallower design.  See "frost protected shallow foundation design" at http://www.huduser.org/publications/destech/desguide.html.

For example the maximum frost depth in Anchorage, Alaska is about 10 feet, but the standard foundation for a heated building has 42 inches of cover, plus 2" subgrade insulation attached to the foundation wall.  Even shallower foundations are allowed with additional (usually horizontal) insulation.

RE: Reducing the "minimum frost" depth

CarlB,

Very nicely done.

RE: Reducing the "minimum frost" depth

I agree with the recommendation of an insulated foundation. The amount of insulation will vary depending upon whether it is a heated or unheated structure, air freeze index and the mean annual temperature for the project location.

You might want to also consider replacing the existing soil with a non-frost suceptible fill material down to the frost depth. The non-frost suceptible fill material actually will freeze faster but will not heave. A non-frost suceptible fill material is defined as one having a very low percentage (say 5% or less) of fine material (passing a no. 200 sieve). This material will reduce the formation of ice lenses since the water can not be transmitted thru the soil particles by capillary action. It is also advisable to keep the soil drained.

Another option is to build a self-supporting structure (with an adequate gap beneath) and support it on frost depth foundations.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources