Transformer
Transformer
(OP)
I need to provide single phase 240V, 125 A to a medical device. Problem is, the only source I have is 3- phase 208V Y.
Suggestions?
Suggestions?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Transformer
RE: Transformer
Note that the load on the 208V circuit will not be balanced. Only two phases will have load current. For a 125A/236V load, the phase current on the 208V side will be ~144A.
There is a variation on the listed single buck/boost transformer configuration that will give closer to 240V on the higher-voltage terminals, but will serve somewhat lower current.
Can you give us some more details on the load equipment?