Generator Neutral Earth Connection

Generator Neutral Earth Connection

Generator Neutral Earth Connection

(OP)
Could anyone please explain the use of a neutral-earth contactor.

RE: Generator Neutral Earth Connection

Take a case where a genset intended for islanded operation also has to to operate in parallel with a utility system.

The utility neutral is solidly earthed at the distribution transformer as is normal practice (in the UK at least). The generator neutral is not connected to ground at the genset because when the genset is paralleled to the utility the the neutral would be grounded in two locations and therefore cause neutral current to flow in the parallel path through the earth. This can cause problems with differential protection schemes which will trip when a certain current is flowing through the earth instead of the neutral.

A similar situation can exist when a generator is one of a number of sets on a common busbar. In this case there will normally also be a single connection from the neutral bar to earth to prevent earth currents.

If the neutral is not grounded for the reasons described above and the genset is also required to operate in an islanded mode during utility outage, then a means of earthing the neutral during islanded operation is required. This is the function of the neutral-ground contactor. It should be open when in parallel with the utility, and closed when islanded.

I'd personally choose a normally closed bar & shaft contactor for this duty because these contactors are usually very robustly constructed and because it will fail 'safe' and ground the neutral. As noted above, in the process of failing it would introduce a code violation by introducing an additional ground, but to my mind that is a lesser risk than leaving the system ungrounded which would render the entire EEBADS design philosophy useless.

----------------------------------

If we learn from our mistakes,
I'm getting a great education!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources