4-20mA to voltage
4-20mA to voltage
OK...embarking on something new here. Figure industrial control guys would know better than the circuit engineering but I figure its a toss up.
I have several 4-20mA current loop sensors, that I need to read with a micro. First off, for a sensor to be using 4-20mA as its signaling, do you simply connect a voltage source to the sensor (most are two wire devices I guess) and then stick a 100 or 250 ohm precision resistor in series to get the voltage? This is not a hobby project so if its suggested to use a unity gain amp section prior to the A/D thats ok. I need something reliable and robust. Cost is an issue of course so not looking for a OEM device to do this, but something I can put on a board layout.
RE: 4-20mA to voltage
In the PLC world we use a lot of loop powered 4-20mA devices. The device is simply wired in series with a voltage source, 24VDC is typical, and an analog input module. A 250 ohm resistor across the analog input terminals then gives you a 1 to 5 VDC input to the A/D.
If you are building your own circuit, the unity gain amp section is probably a good idea, as you will need a high impedance input to the A/D in parallel with the 250 ohm resistor. Another thing to consider would be the use of an analog optical isolator between your input and output circuits.
Hope this helps.
for analog
They are also called optocouplers. There are also isolation amplifiers available, which may be more what you need. Try searching for a existing schematic, or look at the semi-conductor websites for places like Analog Devices, Burr-Brown/TI, Fairchild, etc...