Explosive limits
Explosive limits
Explosive limits
Can someone help refresh my memory on calculation fo Explosive limits?  I have a 200 cubic foot enclosure.  What volume of Isopropyl aclohol liquid would I vaporize to get to 2.5%V/V in that enclosure.
Thanks in advance for your help on this.
RE: Explosive limits
PV=nRT
n=m/MW
m=PxVxMW/RxT
The "partial volume" of IPA = 200 x 0.025 = 5 ft^3.
at 60 F and 14.7 psia
m=(14.7 psia)(5 ft^3)(60.09 lb/lbmole)/[(10.73 ft^3 psia/lbmole/R)(520 R)]
m=0.8 lb
Good luck,
Latexman
I have a related question.  For the hydrogen oxygen inerts,
how is the LEL (lower explosion limit)  and MOC (maximum oxygen content) affected by temperature.
I could find data at room temperature, but I am  looking for the 250°C temperature.
Please start a new thread with a descriptive subject.  If you don't, it'll make searching for it later more difficult.
Good luck,
Latexman