Column Ties

Column Ties

Column Ties

(OP)
I am reviewing a shop drawing where the detailer has shown the lateral ties for a square column as four individual pieces of rebar per tie (one bar on each side of the square tie). Each piece has a hook on each end and all of the reinforcement is enclosed by the ties.

This arrangement looked a little unusual to me. Does anyone know of any concerns or ACI requirements that would prohibit this arrangement?

RE: Column Ties

I would think that the column cage would have more of a tendency to fold over on itself (kind of like a pinned-pinned structure with no x-bracing) because it doesn't have the rigidity of the continuous perimeter tie. Someone would have to add numerous mini-x-bracing in the plane of the ties to keep the cage rigid during handling and pouring. These mini-x-bracing rods or tie wires may cause the concrete to segregate as it is dropped in the form.

I would think that the GC would not be very happy about this situation.

I would require the perimeter tie to be continuous.

RE: Column Ties

Rigidly interpreting ACI 7.10.5 what you describe appears to be acceptable - The only thing found in that ACI section is in the commentary where they say that stirrup hooks should be staggered "where possible" - which is not possible in your case.

We have used this kind of tie for interior bars with columns of 8 or 12 bars (with > 6" clear space between bars) where one end hook is a "J" hook and the other end a standard 90 degree hook.  The thought is that we try to get as much hook as we can by using the J and this allows installation by hooking the J around the long. bar and then rotating the 90 deg. hook onto the other bar.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources