As an EE, this is embarassing, but I don't work with electrical circuits much so ...

I am designing a DC distribution circuit for a meter house. We have a 24 VDC battery charger (Input: 120 VAC) that feeds DC circuits and a set of batteries. If we lose AC to the building (thus, the charger), the batteries back up the 24 V power.

My predecessor used a standard Square-D Load Center, with the charger tied to the Main (30 A breaker) and the batteries off one of the circuit breakers (30 A). If the charger lost power, the batteries would feed back thru the breaker to power the main bus. It works, but the Load Center and breakers are not listed for DC.

I tried to redesign it using DC circuit breakers, with fuses for each circuit. I routed power (+24VDC) from the charger, thru a 30A DC breaker, to the fused terminal strip. This is also connected to a second 30A DC breaker and then to the batteries (+). Thus, when both breakers are closed, power comes from both the charger and the batteries. If you open CB1, power is fed from the batteries, but backward thru the breaker. If you open CB2, power comes from the charger.

Here's a rough idea:

CHARGER-------|CB1|+------------TERMINAL STRIP
                               |
                               +-----|CB2|------BATTERIES



My questions:
1. Is it permissible to feed back thru the Circuit Breaker?

2. If the batteries short out, won't they take both Circuit Breakers with them? Or, should I size the CBs differently?

3. Is this exercise fruitless? Is an AC Load Center suitable for 24 VDC?

TIA,
          . . . Steve

RE: DC Distribution & Circuit Protection

Hello ICman,

I think that it is best to answer qestion # 3 first: A DC circuit should have DC breakers. Even if your voltage is about twenty percent of the nominal AC voltage of the breakers, I think that the breaking capacity of the breakers is very questionable. It may work, but if it doesn't - you will have some legal problems. Is there a DC rating for the breakers? If so, is it in line with your expected short circuit current?

#1  The current direction is of no consequence in an AC breaker. If it can break the DC, it will do so regardless of current direction.

#2  Yes. Choose different ratings so that you get some selectivity in the circuit.

Gunnar Englund
www.gke.org

RE: DC Distribution & Circuit Protection

(OP)
Thanks! I could not find that page on their Website, though I did see some reference to 48 VDC.

Their FAQ seemed to indicate that these were not suitable.

     . . . Steve

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources