power transformer short circuit impedance voltage
hi,
I would like to know the physical meaning of transformer short circuit impedance voltage written on the name plate of transformer as %
Best regards.
Best regards.
RE: power transformer short circuit impedance voltage
“The voltage required to circulate rated current through one of two specified windings of a transformer when the other winding is short-circuited, with the windings connected as for rated voltage operation.” (IEEE C57.12.80)
You might also Google "open circuit test" + transformer and "short circuit test" + transformer.
If we learn from our mistakes,
I'm getting a great education!
If you have a 110 KV/11 KV trafo with 10% impedance, you apply 11 KV on the 110 KV winding with 11 KV winding shorted across the three phases to get 100% rated current on both windings.
The impedance a transformer is measure by the method described by scottyuk above..