Pull Stations

Pull Stations

Pull Stations

(OP)
Building has retail on floor 1 and an apartment on floors 2,3 & 4. Each apartment has a back door that exits to an outside stairway. Do I need to install a pullstation withint he apartments at the back door? The front doors open into a common corridor/stairway with pull stations on each level.

RE: Pull Stations

Before attempting to answer the question a couple of questions:

1) Is the building sprinklered?
2) What is the adopted Fire Code in the jurisdiction?

RE: Pull Stations

(OP)
yes the building is sprinkled and 2002 NFPA 72

RE: Pull Stations

I did not check the codes, but there is no requirement for a pull station in a dwelling unit.

You may want to check NFPA (74??) for the household fire alarm system.

RE: Pull Stations

(OP)
I know there is no requirement for a pull station within a dwelling unit, but there is a requirement for a pull station at every exit from the building.

RE: Pull Stations

Those exits are meant to be path of egress...no path of egress (for public or other residents) passes thru anyone's dwelling unit..

In any case give a call to the local fire marshal's office and you will hear from horses' mouth..one that really counts.

RE: Pull Stations

If the buildings are sprinklered and are constructed using the 2003 International Fire Code a manual fire alarm system is not required.

RE: Pull Stations

stookeyfpe:

Where did you get that? ?

If the building is sprinklered, in most cases 'automatic' detection system (smoke and heat detectors) are not required. Manual station  and in this case waterflow switches are always required where a fire protection system is installed

RE: Pull Stations

See 2003 International Fire Code section 907.2.8.1, exception 2. In Group R-1 occupanices (apartments) only one manual pull station installed at an approved location is required and waterflow shall activate alarm notification devices. These are generally audible alarm devices in the dwelling units.

Note the original post only asked about manual pull stations. That implied (in my mind) that a manual fire alarm system was proposed for installation. This is why I asked if the building was sprinklered.

If the dwelling units are served by an interior corridor an automatic fire alarm system is required. See section 907.2.8.2 of the 2003 International Fire Code.

RE: Pull Stations

(OP)
the building is sprinkled and a pull station is not required within the dwelling unit. thanks for all the advice.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources