Steam boiler fuel oil recirculation

Steam boiler fuel oil recirculation

Steam boiler fuel oil recirculation

(OP)
Can anybody give me any advice regarding back-up heavy fuel oil firing of boilers.
We have a set of six Thompson steam boilers, fed primarily from gas, but the essential back-up system is of heavy fuel oil which used to be used as the primary source of fuel.

The fuel oil is recirculated from storage tanks, to high pressure gear pumps ( to 15 Bar) through filters and heaters ( to 125DegC) to the burners, and while not used recirculated back to tank. The problem is that the temperature of the tanks is above the flash point (66DegC) and has been considered a safety risk, and I'm looking to install a recirculation leg from the burners to the pump suctions. The temperature and pressure has to be kept as is for essential quick change over in case of a power cut.

The problem is that by circulating the oil to the pump suction, the inlet pressure will be dictated by the head of the tanks, which is only 5 metres. I've found that the oil will flash at any pressure/head lower than 2 barg, therefore the oil will flash. What I haven't been able to ascertain is whether the vapour would be significant, and cause pump cavitation wear over time. The oil suppliers have not been forthcoming with data or advice.

I've found that the industry standard is to have low pressure feed pumps from tank to high pressure pumps, this could be an expensive outlay if not necessary.

Any ideas/comments? Thanks in advance.

RE: Steam boiler fuel oil recirculation

In the oil-fired plants where I've worked, there were internal tank heaters that were used to maintain the oil temp at about 120* - 140*F. There was another heat exchanger ahead of the guns that kicked the oil up to firing temp, which was typically 225* or 230*F. During periods when oil wasn't being fired (but could possibly be required on a few hours notice) the oil was circulated at the storage tank temp, just so there wasn't a long section of pipe full of cold oil. (Tough to move cold bunker oil.) Once we were up and running on oil, there was usually enough hot oil being recirc'd from the guns that we'd just shut the tank heaters down.

RE: Steam boiler fuel oil recirculation

The hottest temperature possible is governed by a few considerations: physical limits of the equipment (tank design temperature, pump seals) also the flash temperature of the oil, it is not wise to be at the flash temperature in the day tank!

Regards

Luis Marques

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources