Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Donate Today!

Do you enjoy these
technical forums?
Donate Today! Click Here

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Matador (Mechanical) (OP)
5 Jul 05 23:33
Can someone please give me some information on how to calculate the SCFM for a compressor?

Flow - 1100 acfm
Pressure - 100 psig
Air Temp - 110 F
Altitude - 1600 ft

A formula and sample calculation would be great.


Thanks in advance
zekeman (Mechanical)
6 Jul 05 19:11
scfm=acfm*(p+14.7)/14.7*530/(t+460)
t temp fahrenheit
p psig
Matador (Mechanical) (OP)
6 Jul 05 19:28
Thanks for the formula Zekman.

Would you substitute the atmospheric pressure associated with 1600 ft elevation instead of 14.7?

 
quark (Mechanical)
7 Jul 05 2:20
Visiting the above given threads would have cleared your confusion.

Actually, the equation for conversion of ACFM to SCFM is

ACFM = (SCFM x Pstd x T)/[(P-Psat*RH)x Tstd]

Where, P and T are actual pressure and temperature in psia and Rankine respectively, Psat is the saturation pressure of water vapor at the actual temperature and pressure conditions. Pstd is standard pressure, 14.696psia and Tstd is (460+60)R.

A general standard condition is at 60F temperature, 14.696psia pressure and 0%RH but there are some different values across globe.

When you calculate SCFM these are the things you should consider. However, if you are trying to calculate FAD(free air delivery) then atmospheric pressure comes into picture.

Regards,

Matador (Mechanical) (OP)
7 Jul 05 10:04
I did read the threads and called the compressor supplier yesterday. The compressors in question were purchased from Sullair and what they call standard conditions are 14.5 psia, 68 F, and dry conditions which i assume to be 0 % RH. There is no mention of the altitude being at sea level.

It seems to me they are mixing numbers, They use atmospheric pressure but dry to me signifys a condition after the air dryer.

The actual line conditions after the air dryer are known. I'm trying to determine the difference between the nameplate capacity and the actual. Once I determine the reserve capacity, then I have to size a larger receiver to keep the second compressor from loading and unloading continiously.

 

rorschach (Petroleum)
8 Jul 05 14:56
Compressor manufacturers are very prone to "fudge" thier numbers. Make sure you take thier numbers with a very large block of salt.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close