2005 NEC section 215.2A1

2005 NEC section 215.2A1

2005 NEC section 215.2A1

(OP)
Does anyone find this new section a bit confusing as I do??  It talks about the "grounded conductor", but the tables referenced are the "equipment grounding conductor".

Mike

RE: 2005 NEC section 215.2A1

No. Please read the commentary if you have the Handbook of NEC 2205, which explains it.

Basically, its a new requirements ensuring minimium size of the neutral (grounded) condcutor not less than the EGC.

RE: 2005 NEC section 215.2A1

(OP)
ok.

Thanks rbulsara..

Mike