overspeed limit for hydro generators
For a pelton wheel hydro generator, what is the speed limit to be set on mechanical and electrical overspeed protection ? What is the applicable standard ?
RE: overspeed limit for hydro generators
Doesn't it totally depend on the size of the wheel?
Are you talking a 6 inch one or a 6 foot one?
I didn't know the limit depended on the size.
The machine is 25 MW, 14 pole, 428 RPM with a 60 ton generator rotor and 15 ton turbine pelton runner
In Hydro turbines, the runaway speeds are generally high, of the order of 180% for a 30MW Pelton turbine with 600rpm rated speed (typical).
The governor is expected to limit the speed rise on full load rejection to 110%. Hence, the trip setting for overspeed can be set to 110%, I think. Electrical overspeed setting is normally kept a little lower than the mechanical overspeed setting, say 108%, normally.
Thx Ragunath. That was the info I was looking for. Is there any standard that specifies this ?
