Hi, I looking for a real good formulas for high resistance grounded neutral applications, and figuring correct wire sizes for installation.
fjconair
fjconair
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Hi, I looking for a real good formu
|
RE: Hi, I looking for a real good formu
Or, maybe you're looking how to size the resistor itself. As a minimum it has to be sized for more than the system charging current. Some sources say 5 times the charging current is a good minimum, with 7 to 10 times required to sense ground faults on the 90% of a machine winding farthest from the neutral. Charging current can be estimated or measured, but is on the order of 0.5 to 1.0 ampere/MVA for most industrial installations.
If you're looking for something else, please be more specific.