Separation between Data Equipment and Electric Power Equipment

Separation between Data Equipment and Electric Power Equipment

Separation between Data Equipment and Electric Power Equipment

(OP)
We are currently building a new computer room in an occupied facility. We have found during demolition activities and 600AMP bud duct running within the area of the future computer room.
As the room will have raised floor we are trying to determine if the server racks are going to be impacted by EMF.
What is the minimum separation between electrical equipment and server racks and data cabling.

I did a search within the forums with no luck.

RE: Separation between Data Equipment and Electric Power Equipment

The bus duct should have a relatively low magnetic field associated with it since the three phases are in close proximity and provide a good cancellation effect.

I don't know of a "minimum" separation in terms of NEC or other codes.  "As far apart as practical" is always a good rule to apply.  Data centers often have fairly high current "Power Distribution Centers" sitting right next to server racks and this seldom causes problems if properly installed.  

On the other hand, you don't really want a 600A bus duct running through a computer room unless it has business to do there.  I'd re-route it.  

RE: Separation between Data Equipment and Electric Power Equipment

(OP)
Thanks dpc, for the response. Currently the re-routing is not possible due to the costs and shutdown associated. We check with local electrical inspector and he advised that he does not have any issue with and does not require to be part of the computer room EPO system.

RE: Separation between Data Equipment and Electric Power Equipment

EIA/TIA-568 specifies recommended clearances to minimze EMI. The only NEC requirements pertain to separation of wiring when in the same enclosure as power conductors.

RE: Separation between Data Equipment and Electric Power Equipment

Three thoughts:

1. The bus duct probably does a good job of attenuating or shielding EMF, especially if it is the "sandwich" type (phases stacked directly on top of each other).

2. Buy a gauss-meter ( < $100? ), measure the field at point where the planned equipment would be closest to the bus-duct, and compare the field strength to a survey of other equipment in the same room (or other locations to which you may have access).  The point here is to quantify the problem and establish some sort of basis for comparison.

3. Constructing additional shielding is always an option as well.

JMB

RE: Separation between Data Equipment and Electric Power Equipment

Good answer JBinCA!

RE: Separation between Data Equipment and Electric Power Equipment

Magnetic shielding materials are available that can be fabricated into almost any shape. They are costly however.

http://www.amuneal.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources