The reliability comparison between 3.3 kV versus 6.6 kV supply (Motor)

The reliability comparison between 3.3 kV versus 6.6 kV supply (Motor)

The reliability comparison between 3.3 kV versus 6.6 kV supply (Motor)

(OP)
I plan to introduce the 6.6 kV power supply to HV motors instead of the exisitng that using 3.3 kV for HV motors. And I have some questions about the reliability & cost comparison between 3.3 kV versus 6.6 kV. If you have any recommendations/experience for using 6.6 kV. Pls advise us.

Thank you.

   

RE: The reliability comparison between 3.3 kV versus 6.6 kV supply (Motor)

6.6kV is more popular in power projects in India, though 3.3kV together with 11kV is being used as auxiliary power supply for motors in power plants with unit size of 500MW for some time now.

Generally speaking, 6.6kV motors are more commonly used and hence chance of getting a competetive quote from vendors is better.

RE: The reliability comparison between 3.3 kV versus 6.6 kV supply (Motor)

SUNBCP,
I think that the issue of what is most commonly used is specific to where in the world you are. I am in the US, and of course we have absolutely no 3.3 or 6.6kV! Just 2.3 or 4.2kV all over, and a little 6.9kV here and there.

Seriously though, I do a lot of work in other parts of the world, and in the Middle East for instance what I see is predominantly 3.3kV. with you being in Thailand, I think that you need to investigate the commonality of any motor voltage you intend to use. The availability of replacements and knowledgable service people will be the most important factor. The motor voltage itself has little to do with reliability or even power consumption. As voltage gets higher, the current goes down so the wires can get smaller. However, as voltage goes up the cost of switchgear and controls goes up as well.

"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more."   
Nikola Tesla

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources