(OP)
Hello-

We have an agency enforcing the requirement than ceilings over 2500 SF have a seismic separation joint with a gap determined by the designer?  I can't seem to find anything on that.  Any experience out there?  Thanks.

rd78

RE: Seismic Separation for Suspended Ceilings

FEMA 302, paragraph 6.2.6.2.2.d.

RE: Seismic Separation for Suspended Ceilings

(OP)
Yes, I'm aware of where the requirement is stated (ref'd ASCE 7).  My interest is in how it is implemented?  How is the size of the gap determined?  Is there an aspect ratio requirement, or does anything under 2500 SF meet the requirement?  Thanks.

rd78

RE: Seismic Separation for Suspended Ceilings

If you read that section in FEMA 302, it gives specific separation joint criteria.

"The width of the perimeter supporting closure angle shall be not less than 2.0 inches (50 mm). In
each orthogonal horizontal direction, one end of the ceiling grid shall be attached to the closure
angle. The other end in each horizontal direction shall have a 3/4 inch (19 mm) clearance from the
wall and shall rest upon and be free to slide on a closure angle."

There is no aspect ratio mentioned.  I suspect this is because the requirement for the separation is based on the weight of a 2500 sf ceiling which is the same regardless of which direction your going.

RE: Seismic Separation for Suspended Ceilings

(OP)
Armstrong's detail for the gap shows 6".  I just wanted to know how that was determined.  The Armstrong rep indicated they believe they meet the requirement with this standard gap design.

RE: Seismic Separation for Suspended Ceilings

You can also check out USG grid systems.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources