IP54 Vs. Nema 4X, Which protection is superior?

IP54 Vs. Nema 4X, Which protection is superior?

IP54 Vs. Nema 4X, Which protection is superior?

(OP)
Hi guys,:)

I'm a bit confused to which is superior in protection (degree) Nema 4X or IP54. I have an RFQ to one of pioneering manufacturer of RMU's and I specified therein a Nema4X enclosure (actually that is the strict specifications of the end-user), but the manufacturer insists on doing an IP54 enclosure because according to them its superior than Nema 4X. Need your advice. Thanks

RE: IP54 Vs. Nema 4X, Which protection is superior?

You could always try Google for an explanation of the meanings of the two systems. I just entered "nema ip ratings" and up came about 17,100 hits. Amazing, huh.

http://www.ezscreen.com/ip_ratings.htm
http://www.esis.com.au/NEMAtoIP.htm
http://www.conformity.com/0502/0502understanding.html

IP54 is inferior to NEMA4X. Consensus seems to be that IP65 or IP66 is more-or-less equivalent.

----------------------------------

If we learn from our mistakes,
I'm getting a great education!

RE: IP54 Vs. Nema 4X, Which protection is superior?

The below table was extract from NEMA Standards Publication 250-2003, “Enclosures for Electrical Equipment (1000 Volts Maximum)”

Table A-1
[From NEMA 250-2003]

Enclosure
Type Number    IEC Enclosure
Classification Designation
1              IP10
2              IP11
3              IP54
3R              IP14
3S              IP54
4 and 4X          IP56
5              IP52
6 AND 6P      IP67
12 AND 12K      IP52
13              IP54

This comparison is based on tests specified in IEC Publication 60529

Also not that Table A-1 above provides an equivalent conversion from the enclosure Type numbers in this Standard to the IEC Enclosure Classification Designations.  The enclosure type numbers meet or exceed the test requirements for the associated IEC Classification; for this reason Table A-1 cannot be used to convert from IEC Classifications to enclosure Type numbers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources