Are there any justifications out there to design/size the MDP for the connected load?
Regards,
Regards,
Lutfi
www.cdeco.com
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Sizing MDP for connected load
|
RE: Sizing MDP for connected load
Perhaps the most commonly used exception is
Noncoincident Loads
"Where it is unlikely that two or more noncoincident loads will be in use simultaneously, it shall be permissible to use only the largest load(s) that will be used at one time, in computing the total load of a feeder or service.
Suggest a careful reading of Article 220 would be appropriate if the NEC applies in your area.