Code reference for Transformer Disconnect?

Code reference for Transformer Disconnect?

Code reference for Transformer Disconnect?

(OP)
I have a 480 - 208/120 V inside dry type transformer being fed from an MCC (MCC is located ~100 ft away in different room).  I cannot find in the NEC code a reference stating that a disconnect means is required in the room with the transformer.  Can anyone provide an NEC reference stating that such a disconnect is required?  Many thanks for anyhelp!

RE: Code reference for Transformer Disconnect?

(OP)
Sorry guys,

Found the reference 110.58

Thanks

RE: Code reference for Transformer Disconnect?

Art. 110.58 is applicable to tunnel installations over 600V, which is not your case

RE: Code reference for Transformer Disconnect?

You can't find it because it does not exist. A primary disconnect is not required to be near the transformer.

RE: Code reference for Transformer Disconnect?

I have run into inspectors requiring local disconncets for LV transformers in Masschusetts. I beleive its somewhere included in Mass Electrical Code.

RE: Code reference for Transformer Disconnect?

alehman is correct, as long as the primary feed is properly protected, the disconnect is not required to be added at the transformer.  The one exception is if the transformer feeds directly into a piece of equipment and that piece of equipment is not within 100 feet and in visual site of the MCC, and there is no other disconnecting means between the transformer and the equipment.  You would need to have a local disconnect, often it is less expensive to do so with a non-fused switch on the primary side of the transformer.

RE: Code reference for Transformer Disconnect?

110.58 does exist, in 2005 edition of NEC. Its not a change so it must exist in pervious one too. However it is true that it is for systems more than 600V.

What I posted earlier is also a fact. I also agree that it is not required by NEC but some inspectors do.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources