IS - Grounding Requirements

IS - Grounding Requirements

IS - Grounding Requirements

(OP)
I am designing a barrier for an intrinsically safe circuit.  How can I determine to required screw/wire size for grounding the barrier?

Would I be able to use two #6-32 screws in parallel?

Is this requirement different from the NEC vs. the IEC?

RE: IS - Grounding Requirements

This question is quite dependent on where the application is to be used.

In the US this is governed by UL 1203 or FM 3610.

15.3.5 At least one terminal or connection shall be provided on each barrier or barrier assembly for connecting the barrier circuit to ground.  The grounding terminal or connection shall besized to accommodate a No.12 AWG(3.3mm2)minimum grounding conductor.  The following constructions or their equivalents comply:

a) A No. 8 (4.8mm diameter) wire binding screw that engages the terminal plate by at least two full threads.  The terminal plate shall be no less than 1.25 mm (0.049 inches) thick, and shall be provided with up turned lugs or the equivalent to hold the conductor in place.

b) A pressure-type wire connector complying with the requirements for such connectors.  Soldering lugs, push-in connectors, quick-connects, or similar friction fit connectors are unacceptable.

c) Bolting the barrier to a grounding bus.

The important thing to remember when designing intrinsically safe equipment is the the end design must be the safest possible.  Unlike most codes this some times allows you to break rules.  However, the grounding requirements are quite clear.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources