Isolation of standy generator earthing system
2

Isolation of standy generator earthing system

Isolation of standy generator earthing system

(OP)
Please what is the safest and most cost effective way to keep a 3ph & N + E generator supply isolated (including the generator earthing system) when not in use via the 4* pole c/o contactor? I want a seperate earth and neutral wire to the installation from the earth/neutral star point on the set. I will be installing a separate generator earthing pit.

RE: Isolation of standy generator earthing system

I do not understand why you want to isolate also the N and E but if you insist then you have to use a 5 pin socket that will disconnect all conductors when N & E are disconnected .
Try to convince me why you should do so as after designing tens of systems with one or more gen systems I never had this problem ( except mobile houses).

A.Rash BScEE & PE
a_rash@bigfoot.com

RE: Isolation of standy generator earthing system

(OP)
The standby generator in question is on a large telecomms site, is 200KVA and for the clients reasons needs to be so. It doesn't "plug in" it is hard wired.

RE: Isolation of standy generator earthing system

If it is hard wired then the only thing to do is to use a draw out 4 pole breaker the earth wire in any case you do not disconnect . Only check your local regulations about special requests for cases you install a 4 pole breaker (like special signs you have to place to caution about this kind of breakers).

A.Rash BScEE & PE
a_rash@bigfoot.com

RE: Isolation of standy generator earthing system

hi..
i will use a 4 pole contactor but i won't split the earth wire. i did 3 or 4 installations like this for data/computer center with back-up UPS and never had any problems.

dydt (toronto)

RE: Isolation of standy generator earthing system

Hi Peter Pylon !

I always tend to have a 4 pole mechanically and electrically isolated changeover arrangement in my experience for standby pruposes and have a seperate manually disconnectable earth link arrangement mounted nearby. Merlin Gerin do the breaker set up and Furse Earthing do the link system. The reason for this arrangement is if the earthing of the installation is PME then the supply Co's earth can become severed in a cable fault when the generator may be required for long periods. In this case you could end up having no Earth at the installation! Best to parrallel earths if possible and have a suitable earth system with the genny if you get this problem. Hope this helps....

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources