Feeder Cable Splice Near Swithgear
Feeder Cable Splice Near Swithgear
(OP)
Hi:
Recently a phase conductor on a 3-Ph, 480Vac system suffered some damage due to overtemp caused by a loose breaker terminal lug.
Rather than replace the feeder, we chose to temporarily splice a new conductor length to replace the damaged section that was cut off.
Some folks in my organization think that the splice should have been made futher down stream away from the switchgear and enclosed in an appropriate box.
Others feel that if a fault occurs due to splice failure the feeder will be protected by the breaker.
Comments please...
Recently a phase conductor on a 3-Ph, 480Vac system suffered some damage due to overtemp caused by a loose breaker terminal lug.
Rather than replace the feeder, we chose to temporarily splice a new conductor length to replace the damaged section that was cut off.
Some folks in my organization think that the splice should have been made futher down stream away from the switchgear and enclosed in an appropriate box.
Others feel that if a fault occurs due to splice failure the feeder will be protected by the breaker.
Comments please...






RE: Feeder Cable Splice Near Swithgear
William
RE: Feeder Cable Splice Near Swithgear
RE: Feeder Cable Splice Near Swithgear
I like the idea of the splice away from the switchgear, particularly for high fault currents. That way if you have a fault at a known weak point (the splice) you don't risk the switchboard as well, and the fault current will be lower further away from the board.
I'm not sure about enclosing it. Any splices we have are included in thermoscanning for some piece of mind.
What kind of load and fault currents have you got?
Regards,
Martin
RE: Feeder Cable Splice Near Swithgear
JMB