I am modifying the solenoid valve circuit from "deenrgize to actuate" to "energize to actuate" logic of a feed water regulatin valve at a nuclear station.  I need to add some sort of low current device to monitor the circuit continuity to assure that the solenoid will operate when logic demands it to operate.  Due to real-estate on the control panel my concept to add neon lamps in the circuit is not viable.  Does any one have other possible solution?

RE: 250VDC solenoid valve circuit continuity verification

Is the "de-energise to actuate" part of a fail-safe design? Why change the design if so?

In principle you could bleed a low current, well below the operating level of the solenoid, through the coil and monitor for continuity that way.

----------------------------------

If we learn from our mistakes,
I'm getting a great education!

RE: 250VDC solenoid valve circuit continuity verification

(OP)
Yes it was original fail-safe design which is being modified due to single point vulneribity concerns.

RE: 250VDC solenoid valve circuit continuity verification

I'm confused. If you don't have the space for a pilot light, what kind of monitoring do you want. Can't get more minimal than that! I would prefer a current monitoring system like using a LED in series or solid state relay to operate some monitor.  In either case a zener should be used in parallel with the current monitoring device to maintain operation in case the monitor fails.

RE: 250VDC solenoid valve circuit continuity verification

I am sure you will analyze, thoroughly, what you are doing. If not, please do. In any case, a similar concept is used with "Lock Out Relays" to prove coil integrity. They are also energize to operate devices. Electroswitch makes these relays. They have an LED indicator with a suitable output for a PLC or whatever. You should be familiar with these working at a nuke station.

I looked at making something a while back and can't recall any details without my file at work. Ill try to check and see if I came up with anything creative.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources