Electrical Substation Design

Electrical Substation Design

Electrical Substation Design

(OP)
I am about to start the design of an electrical substation in Jersey City, NJ. I normally design bridges to AASHTO, and am having a little bit of trouble navigating the building and electrical standards. The structure is single story of probably reinforced CMU design.

We have been told by the client that we should use BOCA 1996, and NESC 1999 (National Electrical Safety Code).

Does BOCA reference the Uniform Building Code for structural design and technical specifics? Are the IEEE (Institution of Electrical and Electronic Engineers) standards on substation design normally applicable? I had a look on the IEEE website, and there are a number of standards in relation to fire and seismic design.

Any guidance you can provide will be greatly appreciated.

Michael

RE: Electrical Substation Design

BOCA is a stand-alone model building code just like the UBC is.  They do not refer to one another or depend upon one another.

RE: Electrical Substation Design

Chek the IEEE Std 693-1997, "Recomended Practice for Seismic Design of Substations". This standard replace the former version of std. 693-87.

Notice that there are mayor changes regarding the seismic requirement for electrical equipment, foundation and structural support.  This standard introduce three seismic performance level (high, medium & Low) associated with defined response spectrum curves in lieu of the conventional seismic zone risk used in UBC, BOCA or other civil structural design standard.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources