Hi there .
I was wondering if you can help me with the connection of signal 4-20 MA output from a KROHNE IFC 020 flow transmitter to an analog input card of PLC because i beleieve that the wiring diagramm in KROHNE manual is wrong. The analog input should be treated as 4-wire.
Thank you very much for your time.

RE: Flow transmitter IFC 020

Unless I'm missing something the 4-20mA analog out from the flowmeter---->to PLC should be a two wires (I) & (I+).

David Baird
mrbaird@hotmail.com
Sr Controls Engineer
EET degree.
Journeyman Electrician.

RE: Flow transmitter IFC 020

Power up the meter. Measure the voltage on the 4-20ma output terminals. If the voltage is above 24vdc then yes. You would connect it as a 4 wire to the plc card. If not you will have to use the loop power from the plc.

What kind of PLC are you using?

Just checked the website. It appears they do not make a 24vdc powered signal converter for the 020 model. So it is most likely a 4 wire connection.

Good luck!  Let me know how you made out

Quote: "Its not what you know, its who you know" - anybody trying to find a decent job

RE: Flow transmitter IFC 020

Panou
You need to have an isolated 4-20ma input module at the PLC.  Connect the PLC A/I + connection to d2 (I+)  and PLC A/I - point to d4 (I).  If your PLC has only A/I module with common connection you will have to use signal insolator between the Krohne and the PLC.
See the IFC 020 Connection diagram at:

http://www.krohne.com/html/dlc/SM_IFC020_e_72.pdf
Page 12.
The point is that the Flow transmitter is controlling the 4-20ma output by the (-) connection and most PLC A/I modules does not like it...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources