Air entrapment in instrument sensors

Air entrapment in instrument sensors

Air entrapment in instrument sensors

(OP)
I was just wanting to confirm that air trapped at the face of an instrument sensor designed and calibrated to measure water under pressure, would cause an incorrect or unreliable pressure to be recorded.

Thanks

RE: Air entrapment in instrument sensors

jsearl,
   Gas trapped in a liquid pressure transmitter will cause innacuracy due to the change in head that results. For water this is roughly 100 kPa/10m. It will also slow down response speed as the gas is much more compressible than the liquid. Normally a liquid transmitter will be connected at the lowest point of a pipeline with a continuous drop to allow any gas to escape.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources