Switchgear dangerous incident

Switchgear dangerous incident

Switchgear dangerous incident

(OP)
A few days ago while carrying out some basic maintenance work in a 20kV ring main unit fitted with bushing mounted current transformers the following sequence of events happened:
-While the circuit breaker was in the "open" position and the earth switch was in the "on" position. When we opened the earth switch,at the moment of doing this the bushings became momentarily live with the subsequent risk for the operator, etc.
The three cable bushings had been shorted prior to the opening of the earth switch as a further precaution.
This resulted in the operation of the protection relay which picked up a fault without reaching the trip state thus indicating to us that the bushings only became live for a very short period of time. Approximately 25ms.
Has anybody encountered this kind of problem with ring main units?
I can not name the manufacturer of the switchgear for obvious reasons.
Any information of similar type of occurrences would be of interest.
Thank you all

RE: Switchgear dangerous incident

Do you know for a fact that the braeker operated or that current flowed? Was there any damage? What type of relay is it? Does it use voltage sensing in any way?

It seems possible that operating the earthing switch somehow caused a false operation of the protective relay.

RE: Switchgear dangerous incident

How long was the ground switch in the ON position? (I assume this is the shorting ground for the CT leads)
May not have been long enough, depending on the size of the CTs and the wire length size to the ground switch. Could also be induced currents from some neighboring energized cable running somewhere next to the CT leads.

RE: Switchgear dangerous incident

CGGP:

Assuming that your main is a vacuum circuit breaker,
and the opposite to cable side was live....

if you visualize a capacitor in parallel with each vacuum interrupter you'll see that the grounding switch coupled your system to a virtual neutral point through these capacitors. Opening the switch floated the neutral point to a different potential, and subsequently current flows through the CT's (C.dV/dt).

RE: Switchgear dangerous incident

Be careful quite RMU like a bomb!!

I tried to imaging the situation, if somebody could correct me that fine, I think one of the following two possible problems is exist.

1. The RMU oil insulation is not in good condition or RMU tank was not topped properly, for long use of RMU, you have to maintain the RMU and change the oil.
 
2. Check the earth switch; it might be the knife / contacts is not in proper position, which could cause such a problem.

RE: Switchgear dangerous incident

Hi all
Can you tell me what are the main considerations of IEC in order to have an MCC panel with protection class IP 20 ?
Thanks in advance for your time.

RE: Switchgear dangerous incident

Mazoon is right. It is no joke for RMU (especially at 20kV) to have this abnormal symptom.  It can be either low insulation (oil or SF6-low gas) or mis-alignment of the contact blades.  Have you tried on other similar unit ?  Check with the manufacturer for explanation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources