Interior Pressure and Expansion Joint

Interior Pressure and Expansion Joint

Interior Pressure and Expansion Joint

(OP)
I am calculating wind pressures acting on masonry walls and I have an expansion joint perpendicular to the wind direction.  In this case the wall is experiencing only windward or leeward pressure but I am wondering if I should also account for additional interior pressure.
Thanks a lot
Kris

RE: Interior Pressure and Expansion Joint

Yes - Masonry walls are typically Components in Cladding and should be designed as such with the appropriate external and internal pressure coefficients acting simultaniously for the worse case forces.

RE: Interior Pressure and Expansion Joint

(OP)
Thanks Willis, and that's what I did for cladding but I meant the total horizontal wind pressures for MWFRS.
Thanks

RE: Interior Pressure and Expansion Joint

When you look at total wind pressures for MWFRS you find the force over the entire building.  Internal pressures are always both acting either inwards or outwards and therefore when you sum horizontal forces they cancel out.  

Windward --> | <--internal  internal ---> | Leeward -->

Internal forces cancel and leave Windward + Leewards for building frame design.

RE: Interior Pressure and Expansion Joint

You would include it if you have the perpendicular expansion joint as you describe.  The internal pressure can only "cancel out" if the building is whole.  With an EJ through it, the windward half would experience the external plus the internal as the internal pressure cannot be resolved across the joint.

RE: Interior Pressure and Expansion Joint

(OP)
Thanks JAE. It is correct what you saying

RE: Interior Pressure and Expansion Joint

Good point.

RE: Interior Pressure and Expansion Joint

I have a question, then...

In this case, on the windward wall, the internal pressure is acting in the same direction as the wind or opposite?

RE: Interior Pressure and Expansion Joint

(OP)
Zo40
I took it as a summ of internal+external pressures so as they act in the same direction.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources