PanelView 1000 Plus communication to ControlLogix?

PanelView 1000 Plus communication to ControlLogix?

PanelView 1000 Plus communication to ControlLogix?

(OP)
I am communicating from a etherNET/ip card with a controllogix 5561 CPU (Rslogix 5000) to a panelview plus 1000 (RSView studio machine edition)

Now my problem is that the values display in the panelview are in error so there is no communication between the touch screen and the plc.

From my laptop in rslinks, i can see all items and ip adresses are configured ok.

The only thing im not sure of is how does the panel view know that it has to send and receive information from the plc. Where do you tell it (look at this plc at this ip adress) didn't see when in the software to do this??

any ideas anyone???

Thank
Ray

RE: PanelView 1000 Plus communication to ControlLogix?

The communications path from the PanelView to the PLC is configured in RSView when the application is developed, and becomes part of the runtime file which is downloaded to the PanelView.

There are Local and Target settings for RSLinx Enterprise in RSView.  The Target tab settings are a view of the network as seen from the device (PanelView), that the application is downloaded to, and must be correct.

RE: PanelView 1000 Plus communication to ControlLogix?

(OP)
Yep finally got it.
Thanks

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources