Neher-McGrath
Neher-McGrath
Neher-McGrath
I would like to know if all of the cable sizing tables in NEC 2005 are based on the Neher-McGrath method.
Thank you
hidalgoe
RE: Neher-McGrath
Yes, in general.
RE: Neher-McGrath
The program AmCalc is based in the Neher-McGrath method.
By inspection of the result in the enclose table, we could conclude that the values from the NEC ampacity table and the calc using the Neher-McGrath method have insignificant deviations.
http://www.calcware.com/NEC%20Tables/NEC%20310-77.pdf