Can someone give me quidance on the specifications of ANSI C37.41 clause 7 as regards loadbreaking requirements.
Being in the UK we work to IEC specs.

RE: ANSI C37.41 loadbreak

Quote (IEEE Std C37.41):

   7. Load-break tests
7.1 Procedures common to all load-break tests
Devices, unless they incorporate a load-breaking means, have no load-break rating. Load-break test procedures for devices with load-breaking equipment shall be as specified in Clause 4 and in Clause 7

Disconnect switch are primarily used for closing, opening, or changing the connections in a circuit or system or for purposes of isolation.

HV Disconnect switches It has no have interrupting rating and is intended to be operated only after the circuit has been opened by some other means, such as by a circuit breaker.  However, HV disconnect switches if equipped with interrupting device attachment may be capable to be used with limited interrupting capability for making or breaking specified current.  (See sample in picture below)



MV switches under certain ampacity limit may have limited interrupting rating without any attachment.

I hope this help.

PS:Beware that the ANSI and IEC switches are not compatible in term of conformance with typical spec.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources