150kVA ROTARY UPS FAILURE

150kVA ROTARY UPS FAILURE

150kVA ROTARY UPS FAILURE

(OP)
Gents,
I have a 150kVA HITEC rotary UPS that when synchronised to the busbar with another machine of the same make and rating does the following:
1. Takes up a large proportion of the connected load.
2. Pulls all the load to itself.
3. Drops the load and starts running on high frequency.
Do you have any idea of what the cause(s) of these may be?
HELP!!!

RE: 150kVA ROTARY UPS FAILURE

Did it used to work correctly and just start this behavior, or is this a new installation?

RE: 150kVA ROTARY UPS FAILURE

(OP)
DPC,
thanks for the reply.
It didn't just started this behaviour. The machine has been down though functional as it was not possible to synchronize it unto the vital load busbar with the other machines. And when it was eventually done, it dropped the load.
However, as at yesterday, it stopped taking any load permanently. It would take load for about a second and drop it.
Any ideas?

RE: 150kVA ROTARY UPS FAILURE

Do you have the voltage regulators interconnected to share the reactive load?

I am assuming that electric motors turn the rotary unit, if the motors are combustion engines you will need additional control to share real power too.

See the following link for more details. http://www.basler.com/php/download_page.php?section=regulation#PRS210

RE: 150kVA ROTARY UPS FAILURE

(OP)
Sorry, I had to take some time off.
DPC, the machine started this behaviour recently

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources