I am doing vibration analysis, using the CSI 2120 analyzer, and have noticed that all the 3000 rpm motors (50Hz) in one of my departments suddenly showed an increase at 40 to 52 times running speed with 2 times line frequency sidebands. In acceleration it went up from 0.07 to 0.55 g's. I then remembered that the transformer feeding this section blew a coil and was replaced with another one. I assume that something in the transformer is reacting to what is probably the rotorbar frequencies in the different motors. Is this serious, what does it tell me about the condition of the transformer, and why the increase?
Regards from South Africa
Regards from South Africa





RE: Electrical frequencies, what do they mean?
This does not match your scenario of course, where all 2-pole motors increased at once (unless there has been a drastic change in temperature which might affect the alignment of all of them... or maintenance shutdown where all where tampered with?)
The power supply would seem to be the only common link among different motors. The only remotely-possible contributors associated with the power supply in order of decreasing likelihood would seem to be:
1 - Increased voltage.
2 - Imbalanced voltage
3 - voltage harmonics? (not too likely).
4 - frequency - I seriously doubt you had a change in frequency.
If you are convinced there is a problem with the power supply I'd recommend checking all three phase-to-phase and phase-to-ground voltage magnitudes.