open/closed transition switching

open/closed transition switching

open/closed transition switching

(OP)
Our regional electric utility will only allow Open Transition switching when they supply a customer who has a double-ended substation. This seems perfectly logical to me, and in fact I am not aware of any scenarios where a Closed Transition arrangement would might be preferred.

After the manufacture and installation of our new main sercvice (using a double-ended 4160 Volt substation), and half-way thru the start-up testing, the manufacturer now states that the set-up of the GE SR750 relays they have used on all of the breakers, including the Main,Tie, and other Main, will not prevent closed transtion.

Help? Does this make any sense to anyone out there?

RE: open/closed transition switching

Firstly, open transition implies a temporary loss of power.  this is often unacceptable so closed transition is sometimes used to avoid any interruption of power.  Closed transitions are fairly common, but have problems related to high fault currents and sometimes synchronizing/phase shifts issues.  

Secondly,  the SR750 is basically a feeder protection relay providing overload and short circuit protection (plus a bunch of other features).  It can be programmed to provide some automatic and manual transfer logic, but I would never expect a manufacturer to program an overcurrent relay to prevent closed transition unless this requirement was explicitly specified when the equipment was purchased.  

To reliably prevent closed transition, the mains and tie should be electrically interlocked, via breaker auxiliary switches, or preferably mechanically interlocked via a Kirk Key interlock system, or both.

So it all makes sense to me.  What seems to be missing is the translation of the utility's requirement into a engineering specification.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources