Size of earthing cable for a drive of 700 A

Size of earthing cable for a drive of 700 A

Size of earthing cable for a drive of 700 A

(OP)
Hi,

Basically what should be the size of the earthing cable for a drive 700A capacity driving a 400 k W motor @ 400 V 50 Hz.
I am using a 300 mm^2 copper cable on the power sides.
I trust that it should be at least the size of the power cable to sustain the current under fault condition.
Furthermore, the manufacturer of the VSD is requesting an earthing cable between the VSD and the motor.

Bob

RE: Size of earthing cable for a drive of 700 A

You can calculate the min cross sectional area using:

S >= (SQRT(I^2t))/k

S = Cross sectional area of earth cable
I = Fault current
t = disconnection time
k = constant determined from tables related to initial temp of conductor & type of cable

(To BS 7671)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources