chiller outlet temperature
hi everybody
according to the inside condition,we are calculating the supply air temperature.what is the formulae for find out the supply (chilled)water temperature from the chiller for the supply air from the AHU.say if i get 13 deg C the chilled water temperature is 8 deg C. how?
RE: chiller outlet temperature
ROGZOG
In that way, on maximum load there will be say 6 degrees supply and 11 degrees return. These are values you neeed (maximal load) to size your AHU heat exchanger.
1) specify room conditions;
2) calculate room load;
3) specify CW supply & return temps (i.e., when designing the CW system);
4) select Fan Coil Unit size by applying the above info to the FCU manufacturer's sizing charts.
If some FCU(s) are already owned, and needed is to build a CW system to suit, then use FCU sizing charts to work backwards to find the needed CW temps. But the FCU is the tail to the CW system (the dog) - be careful that such an approach does not produce an uneconomical CW system.
