change condenser
change condenser
(OP)
I need change condenser in wall cabinet (with capillary tube as metering device).Old condenser was consisting of 5 circuits. New condenser consist of 3 circuits.
Another parameters of condensers are equal. When I charged by R22 and run system the compressor was flooded. Why?
What should I do for correct working of system?
Thank for any advice.
Another parameters of condensers are equal. When I charged by R22 and run system the compressor was flooded. Why?
What should I do for correct working of system?
Thank for any advice.





RE: change condenser
Capillary systems are critical charge systems. That means the charge must be measured very carefully.
Your cap tube quantity and loading has obviously changed or you did not size them correctly in the first place.
Suggest that you review the system and focus on cap tube sizing.
Good Luck
pennpoint