Natural Gas Pipe sizing for 6,000,000 btuh
Natural Gas Pipe sizing for 6,000,000 btuh
(OP)
Could I get some help in verifing what N.G pressure would be required to move 6,000,000 btuh through 3" pipe 450 linear feet. I need 1-2 psig at the recieving end. Would 5 psig be adequate.





RE: Natural Gas Pipe sizing for 6,000,000 btuh
---KenRad
RE: Natural Gas Pipe sizing for 6,000,000 btuh
The pressure drop would be less than 2 PSI in a 2" line. Looks like you've got yourself a nice safe situation.
RE: Natural Gas Pipe sizing for 6,000,000 btuh
---KenRad