Why does SR469 Show 4000% Current Unbalance

Why does SR469 Show 4000% Current Unbalance

Why does SR469 Show 4000% Current Unbalance

(OP)
I have three SR469's each feeding identical motors (250 HP, 575V).  The current readings appear correct and visual inspection of the CT's appear correct (polarity & wiring - although wiring has not been confirmed by electrically tracing).

All three show current unbalance readings in the 2500%-4000% range.  Any ideas what is wrong?

Voltages are approx. 612,608,610.

Thanks for any help.

RE: Why does SR469 Show 4000% Current Unbalance

What are the current readings?
Seems strange to have such high unbalance readings since using the NEMA method of calculating you can only have a maximum of 100% unbalance (loss of a leg). Although, I never used these particular relays.

RE: Why does SR469 Show 4000% Current Unbalance

You probably have one of the CTs hooked up backwards.

"Venditori de oleum-vipera non vigere excordis populi"

RE: Why does SR469 Show 4000% Current Unbalance

(OP)
I thought so too but all three motors show the exact same problem.

Must be a CT wiring problem?

RE: Why does SR469 Show 4000% Current Unbalance

You might check the phase sequence configuration setting in the SR469.  I believe it can be set to either positive or negative phase sequence.  I have seen similar issues corrected when this setting is reversed.  

You can also check the SR469 power and var readings.

RE: Why does SR469 Show 4000% Current Unbalance

Is this a new or an old installation?

One of 4 possibilities:

1. Fault in the primary circuit
2. Fault at CTs
3. Fault in wiring (between CTs and relay)
4. Fault at Relay

 
Number 1 is not a possibility, because it happens on three different places. Thus your fault can be either at the CTs, the wiring, or the relay. Because this fault occurs on three different places, it has to be a common problem on all the places.

What kind of scheme do you use on this relay? (residual connection, core balance method, etc.) And are there not a metering feature on this relay that shows the different line currents and the unbalance current?  Many times, by just looking to these currents, you can almost guest where your problem is or what kind of problem you have.

The most common problems I have encountered on this kind of fault is wrong connections at the back of the relay:
Connected on the wrong place/location.
Connected on the wrong element (1A instead of 5A and vice versa.)
Also, if you have a connection/test block, makes sure it is bridged out at the correct places.

RE: Why does SR469 Show 4000% Current Unbalance

With the current imbalances you posted the motor must have melted down. We can assume that this is erroneous data. I installed a CT with 115AC exciter current one time.

RE: Why does SR469 Show 4000% Current Unbalance

(OP)
Unfortunately, I am not on site anymore so my information is limited.

I believe the currents were relatively balanced (less than 1%).  I will check some more settings and try changing the system phase sequence to ACB from ABC to see the effect.

Thanks for all the responses thus far.

RE: Why does SR469 Show 4000% Current Unbalance

The phase rotation is specified incorrectly in the Multilin 469.  Change that and you'll see the correct imbalance.

RE: Why does SR469 Show 4000% Current Unbalance

Forgot to mention; star for dpc

RE: Why does SR469 Show 4000% Current Unbalance

(OP)
Thanks Laplacian, you are correct.  Checking the phasor values on the Multilin is the best way to trouble shoot and confirmed the phase rotation was actually ACB not ABC as originally set.  Switching corrected the problem.  Now onto the next challenge.......

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources