Flash Tank Sizing Standard
2

Flash Tank Sizing Standard

Flash Tank Sizing Standard

(OP)
Does anyone know any information pertaining to sizing Flash Tanks for steam systems.  I am wondering if there is a  standard that I must adhear to or if sizing a Flash Tank is simply left up to what the distributer's specs call for.  

Thanks for any help.

RE: Flash Tank Sizing Standard

I believe that there are, at least, two resources. One is ASHRAE HANDBOOK, and other is one North Amercia Valve Vendor's handbook. As I am out of home country for the business, sorry for no further detailed information available.

RE: Flash Tank Sizing Standard

Just checked with some files in my laptop, it is recommended that you refer to S10.14 of ASHRAE HANDBOOK.

RE: Flash Tank Sizing Standard


You could try the Canadian Boiler, Pressure Vessel and Pressure Piping Code B51-97, Part 1

RE: Flash Tank Sizing Standard

hadams...

The people at Penn separator have always been helpful to me

http://www.pennseparator.com/

They offer sized systems based on the boiler capacity, pressure and expected blowdown rate.

I had some ancient ASME papers, from the 1940's on this topic.....developed by a former Stone & Webster Vice president.....I had 'em......but I lost them

I am aware of no recent engineering textor article on this subject.

MJC

  

RE: Flash Tank Sizing Standard

An internet source for flash tank sizing is:

http://www.sugartech.co.za/rapiddesign/flashvessel/index.php

One of the more important governing factors is the limiting of the upflow velocity of the steam vapor to prevent entrainment of moisture droplets.

There is a good discussion of this issue in another forum in this site, so you might try a search in Eng-tips.

rmw

RE: Flash Tank Sizing Standard

(OP)
rmw -

Your internet link was quite helpful.  The National Board of Boiler and Pressure Vessel inspectors provides a document called "A Guide for Blowoff Vessels" where they identify a good target velocity for the steam vapor of 11 ft/sec to allow for proper seperation.  

https://www.nationalboard.org/NationalBoard/Publications/Pdf/nb27.pdf

Im not having any luck locating the discussion you made reference to (I'm rather new on this website) and I was hoping you could point me more in the right direction.  Thank again for your help.


_________________________________
Henry B. Adams, III
Clemson University, ME Undergrad
Spirax Sarco Inc.
www.spriaxsarco.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources