Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...I have found your site brilliant. What makes it good are the people that contribute to the site..."

Geography

Where in the world do Eng-Tips members come from?
Hugh3 (Specifier/Regulator)
17 May 05 8:07
Does anyone know the rules on devicenet installations in Cl. 1 Div. 2 areas??? We have plug connectors to various devices (which are rated Cl. 1, Div. 2) and I am told I'll need "lock fast" jackets over connectors (to avoid any chance of them falling out) but I can find no written evidence of this.  These plugs are made such that they disconnect conductors before they are exposed.
rbalex (Electrical)
17 May 05 10:10
While I'm familiar with classified locations I wasn’t familiar enough with DeviceNet to respond to your question immediately.  I did a bit of research at www.odva.org to get a better handle on it. What I found would lead me to believe it would not be an acceptable application as you have described it so far. But there is good reason to believe an acceptable installation can be made.

I’m using the 2002 edition of the NEC as the basis; conceptually, 2005 applications would be the same. The applicable section would be 501.14, but it refers back to the general Sections for specific applications.

Acceptable wiring methods for Class I, Division 2 are listed in Section 501.4(B).  One of the methods is “Nonincendive field wiring” described in 501.4(B)(3). Read it carefully as there is a fair amount of documentation necessary to apply it. I found several acceptable power supplies listed on the ODVA site under the DeviceNet Catalog (on the left) then Products by Category/Physical Layer Components - Power Supplies.

The connectors you described initially are not acceptable alone. It would still be considered a “make-and-break” contact and need to be installed either under 501.3(B)(1) or possibly, 501.3(B)(6) unless it is covered under nonincendive field wiring.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close