cold joints in retaining wall heel slab

cold joints in retaining wall heel slab

cold joints in retaining wall heel slab

(OP)
Question:
I have another concrete cold joint problem. This one is on the cantilever retaining wall heel slab. The base slab is design for 24" thick. Cold joint is at 10" from ground. My gut feeling is we need to do something. Can somebody tell me what are the remediations other than saw-cutting and replacing it? What about pressure-injetting epoxy to fill up the voids at the cold joint? Please advise. Many thanks.

RE: cold joints in retaining wall heel slab



Have you taken any core samples and tested them to see if they fail along the cold joint plane?

RE: cold joints in retaining wall heel slab

(OP)
As a matter of fact, we did try to take a core sample but it broke at halfway.

RE: cold joints in retaining wall heel slab


Longhornse

Have you done an ultra sound test to determine the extent of the voids with in the heel?



RE: cold joints in retaining wall heel slab

(OP)
Roadbridge,

No, we haven't. I don't think we have any intention of doing that. Do you think it will help? When the core broke halfway, I was almost certain that it was due to the cold joint. An ultra sound test may not be able to tell me a lot. It would if there is honeycombing in the slab. Please correct me if I am wrong. Thanks.

RE: cold joints in retaining wall heel slab

Sounds like you have a 14 inch thick footing on a 10 inch levelling pad.  Perhaps you can dowel the two together.

RE: cold joints in retaining wall heel slab



Have you rechecked the design assuming it to be just 10' thick heel.
Injecting epoxy, can you be sure it will work?

RE: cold joints in retaining wall heel slab

This cold joint dose it run the entire lenght of the footing or is localised in one area.

Keano1 may have hit on some thing at looking at the design again, but see how the 14' section reacts in the design rather than the 10'.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources