system bonding jumper

system bonding jumper

system bonding jumper

(OP)
I have a 3-phase 480 volt to 120/208 volt Y xfmr. There is a copper strap that bonds the core to the enclosure. Do I have bond XO to my equiment grounding conductor brought from my 480 volt panel and also building steel and water pipe system? If I don't will I have unsafe system?

RE: system bonding jumper

The answer is yes, you will have to terminate the equipment grounding conductor for the 480V feeder at one of two locations; 1) the grounding lug at the conduit insulating bushing or 2;) at the ground lug inside the transformer enclosure.

However it is very important as you already mentioned, that this equipment grounding conductor can not substitute the required grounding electrode conductor going to the nearest ground electrode (pipe, strutural steel, etc.)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources