Cable Armour of the Teck Cables as Barrier of Power/Comm Cables

Cable Armour of the Teck Cables as Barrier of Power/Comm Cables

Cable Armour of the Teck Cables as Barrier of Power/Comm Cables

(OP)
Can we consider an cable armour of the TECK cables as a some kind of barrier, and install power and comununication cables on the same cable tray ? What American and Canadian Standards say about that ?

RE: Cable Armour of the Teck Cables as Barrier of Power/Comm Cables

Our local Ontario electrical inspector's interpretation of the Canadian Electrical Code is that a separate barrier is required between MV and LV cables even though they are Teck armoured.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources