My contractor want to use radiant ceiling tube heaters for bowling alley "common" area. I need to provide ventilation for fresh air & cooling. In the cold months the heaters will be on & so will the fresh air system. How much will this air movement mess the radiant ability to heat?





RE: Radiant Ceiling heat & ventilation
RE: Radiant Ceiling heat & ventilation
Generally speaking the air movement will increase the radiant's ability to heat the space.
RE: Radiant Ceiling heat & ventilation
Some gas radiant systems have no flue (a bit dodgy-applicable to the UK ) but if you ventilate the space to about 2AC (Don't quote me on that exact figure), then no flue is required.
I generally use flues and in addition, If I need fresh air, then this is tempered before supply to the space.
The heat output from a radiant panel is mostly radiant (depending on the surface temperature) Typically 90% radiant and 10% convective for the higher temperature models. If a 'draft' is incurred, then a greater output on the convective component will be realised...i.e. the heat output could go up slightly.
You should supply tempered air to offset the potential effect of cold drafts.