Debonded Strands in Pretensioned members

Debonded Strands in Pretensioned members

Debonded Strands in Pretensioned members

(OP)
This question arises from a previous post on designing a member with ConSpan and the discussion on the effects of debonding.

In this discussion it was suggested that strands could be debonded at midspan of a member, presumably while being bonded at each end of the member.

Can anyone explain how this debonding is achieved?

Is the strand simply greased or sheatherd over the length that is to be debonded, so that it acts like an unbonded post-tensioning tendon over this length?

 
Or is the force in the strand over the debonded length released in some way so that there is no prestress force in the strand as well as the greasing/sheathing to debond it over a specified length?

RE: Debonded Strands in Pretensioned members

The de-bonding of the strands in the midspan could be done using same methods as for ends of the beams i.e. by sheathing or greasing. Typically this is being done with the top strands, and pockets should be left for cutting the strands prior to the release.
In case when sheathing is used, the unused (unstressed) sections of strands could be grouted after cutting to be used as part of reinforcement.

RE: Debonded Strands in Pretensioned members

(OP)
wiktor

I agree that this is the only way to do it to achieve what is referred to as debonded strands in pretendioned members. It is not sufficient to simply debond the strand as would be the case with unbonded post-tensioning, it must be released/cut also so that there is no force in it over the debonded length from the stressing operation.

The regrouting would not be all that effective as there would be a significant development length either side of the cut.

I was wanting to make sure that people using internal debonding realised that it involved more than simply greasing the strand to ensure that it was not bonded to the concrete. That the term "debond" in pretensioning means no pretension force in the strand and that it needed to be specified properly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources