LOW VOLTAGE SWITCHGEAR TESTING

LOW VOLTAGE SWITCHGEAR TESTING

LOW VOLTAGE SWITCHGEAR TESTING

(OP)
I have to witness a low voltage switchgear factory test soon.
I only have project specifications which do not say much.
I like to know if there is any literature on line where I can look up  for some of the important testing requirements

RE: LOW VOLTAGE SWITCHGEAR TESTING

The specifications should identify the standard the switchgear falls under. This will tell you the test procedures and acceptance criteria.

RE: LOW VOLTAGE SWITCHGEAR TESTING

You can lookup neta "International Electrical Testing Association" online but I think their viewable specs are limited.

RE: LOW VOLTAGE SWITCHGEAR TESTING

If there is nothing in the specifications on testing, only the specified standards would apply unless you modify the contract.

In the U.S., UL 891 would typically apply for low voltage switchboards. If the specs require switchgear construction per ANSI standards, ANSI C37.20.1 and UL 1558 would apply. You must read the specs very carefully to determine which standards apply.

Any of these standards will require insulation resistance (megger) testing of the bus and control wiring, AC insulation strength (hipot) test, ground fault system test if applicable, operation of all circuit breakers and switches and functional testing of control schemes and interlocks.

NETA testing is much more comprehensive but would apply only if it is required by the specifications. NETA tests are normally intended to be performed after installation rather that at the factory.

RE: LOW VOLTAGE SWITCHGEAR TESTING

As mentioned above the switchgear that you are going to witness the test, must/should adher to a standard. You can have a look at IEC/EN 60439-1 which will give you fair idea about the different type of tests need to be run in a switchgear. This standard talks about the type tests & gives some idea about the routine tests also. Since you mentioned abt the project spec, I think you are going to first time launch the product. So what you need is to perform/witness a set of type tests, which this standard talks about in details.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources