hot line power being drawn through ground

hot line power being drawn through ground

hot line power being drawn through ground

(OP)
A customer sent back a motor for repair claiming it intermittently wouldn't run.  We took it apart and found nothing suspect.  The only thing we saw was the customer had put his own plug on the cord and had wired it wrong.  The hot lead for the motor was connected to the ground of the plug.  The ground wire for the motor was hooked up to the nuetral blade of the plug.  So, if the customer's receptacle was wired correctly, this motor would have pulled its power through the ground circuit.  Would this cause some intermittent operation?

RE: hot line power being drawn through ground

It should not have worked at all, the way you describe it.

William

RE: hot line power being drawn through ground

To summarize...

MOTOR     Facility
 HOT       GROUND
 NUET       HOT
 GRND      NUET

Yes, it would be sinking its consumed power to earth.

Yuck! BAD, Bad, bad.

(never mind as a kid I ran a 3hp compressor this way, dirt would steam if wet)  

The intermittant-ness could be a lot of things with these inept plug wirers.

Did they wire their facility?  <shudder>

RE: hot line power being drawn through ground

No, it would be sinking its consumed power through the equipment grounding conductor.  Possibly overheating the grounding conductor and its connections, causing intermittent open circuits or maybe the voltage drop through the undersized return conductor was just too much for reliable operation.

RE: hot line power being drawn through ground

(OP)
Yes, Itsmoked, you have the summary correct.  The motor does run in our plant.  It is scary what we see from some of our customers.  I'm thinking this guy probably wired the receptacle and there's a bad connection in it.

RE: hot line power being drawn through ground

If you visit their plant aways note the non-metalic fire exit routes!  :)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources